During phase finding the motor
slowly and smoothly turns 2 turns one way, then reverses
and turns about 1 turn the opposite direction.
Here is the report, as well as the
axis settings and motor specs:
REPORT (autophasefindfast.c)
0 Position = -2178 PhaseAngle = 1.131900
1 Position = -18562 PhaseAngle = 6.132500
2 Position = -18562 PhaseAngle = 6.055300
3 Position = -2178 PhaseAngle = 1.040500
Counts per rev = -16384
Counts per cycle = -3276
Counts per cycle (rounded)= -3280
invDistPerCycle (rounded)= -0.000304878049
Commutation offset = 512
Input Gain Specified = 1.000
Axis Settings:
ch0->InputMode=ENCODER_MODE;
ch0->OutputMode=BRUSHLESS_3PH_MODE;
ch0->Vel=4000;
ch0->Accel=4000;
ch0->Jerk=4e+06;
ch0->P=0;
ch0->I=0.0001;
ch0->D=0;
ch0->FFAccel=0;
ch0->FFVel=0;
ch0->MaxI=200;
ch0->MaxErr=1e+06;
ch0->MaxOutput=200;
ch0->DeadBandGain=1;
ch0->DeadBandRange=0;
ch0->InputChan0=8;
ch0->InputChan1=0;
ch0->OutputChan0=8;
ch0->OutputChan1=0;
ch0->MasterAxis=-1;
ch0->LimitSwitchNegBit=0;
ch0->LimitSwitchPosBit=0;
ch0->SoftLimitPos=1e+09;
ch0->SoftLimitNeg=-1e+09;
ch0->InputGain0=1;
ch0->InputGain1=1;
ch0->InputOffset0=0;
ch0->InputOffset1=0;
ch0->OutputGain=1;
ch0->OutputOffset=0;
ch0->SlaveGain=1;
ch0->BacklashAmount=0;
ch0->BacklashRate=0;
ch0->invDistPerCycle=0.000304878049;
ch0->Lead=0;
ch0->StepperAmplitude=20;
ch0->iir[0].B0=1;
ch0->iir[0].B1=0;
ch0->iir[0].B2=0;
ch0->iir[0].A1=0;
ch0->iir[0].A2=0;
ch0->iir[1].B0=1;
ch0->iir[1].B1=0;
ch0->iir[1].B2=0;
ch0->iir[1].A1=0;
ch0->iir[1].A2=0;
ch0->iir[2].B0=0.000769;
ch0->iir[2].B1=0.001538;
ch0->iir[2].B2=0.000769;
ch0->iir[2].A1=1.92076;
ch0->iir[2].A2=-0.923833;
Motor Specs:
Unimotor HD 089EDB400BACAA
Type Unimotor HD
Frame Size (mm) 089
Voltage E E - 220V
Magnet type D D - High dynamic
Frame Length B
Speed (min-1) 40 4000
Brake 0 0 - Not fitted
Connection type B B - Power and Signal 90°
rotatable
Output shaft A A - Key
Feedback device code CA CA - 4096 ppr Incremental
encoder
Inertia & thermistor A A - Standard + PTC
thermistor
PCD 100 100 (FF 100 / 80)
Shaft Diameter 190 19j6 x 40.0 .
Fan box -
Insulation class F
Nominal characteristics
Motor Ambient Temperature (°C) 40 Drive Fsw
(kHz) 12
Motor Stall Torque (N.m) 5.50 Stall Current (A)
7.90
Rated Torque (N.m) 4.55 Nominal Current (A) 6.5
Motor Peak Torque (N.m) 16.50 I max (A) 23.57
Rated Power (kW) 1.91 Kt (Nm/A) 0.70000
Winding Thermal Time Constant (s) 93 Ke
(V/kmin-1) 42.75
Number of Poles 10 R (ph-ph) (Ohm) 0.79
Maximum Cogging (N.m) 0 L (ph-ph) (mH) 5.97
Inertia (kg.cm²) 1.61 Weight (kg) 4.40
Ingress Protection Level (IP) IP65
David.
On 11/13/2016 2:59 PM, Tom
Kerekes
tk@...
[DynoMotion] wrote:
Hi David,
Do you have a motor specification?
What does the report of AutoPhaseFindFast.c indicate?
What happens during phase finding?
What are your Axis settings?
I'm trying to setup some Emerson Unimotor 3ph
brushless servos with SnapAmp, but can't get them
to respond properly.
The autopahsefindfast.c works good to slowly move
the motors and determine offsets, but step
response testing only gives nasty ticking of the
motors regardless of any settings I try. The motor
specs are very similar to the Baldor servo motors
I often use so I am at a loss as to what may be
wrong.
Any suggestions are greatly appreciated.
David.
This email has been checked for viruses by Avast
antivirus software.
www.avast.com